Hi - setting up chiller to run form P4 along with a heater. The user manual is not clear about the shut off point for cooling and leaves the calculation ambiguous.
Examples:
Nominal: 25
Hysteresis: 1
Cooling Diff: 0
Calculated points
Heat Start: <24.5
Heat Stop: 25.5
Cool Start: (Nominal + (5/6 * Hysteresis) + Cooling Diff)
>25.83
Cooling Stop is it:
1 - Cooling Start - hysteresis = 24.83
2 - Cooling Start - (hysteresis/2) = 25.33
3 - Nominal - (hysteresis/2) = 24.5
??
I feel that the user manual needs to be updated here.
@Vinny@GHLUSA
@Gaël
Examples:
Nominal: 25
Hysteresis: 1
Cooling Diff: 0
Calculated points
Heat Start: <24.5
Heat Stop: 25.5
Cool Start: (Nominal + (5/6 * Hysteresis) + Cooling Diff)
>25.83
Cooling Stop is it:
1 - Cooling Start - hysteresis = 24.83
2 - Cooling Start - (hysteresis/2) = 25.33
3 - Nominal - (hysteresis/2) = 24.5
??
I feel that the user manual needs to be updated here.