What a devastating situation. Great attitude about it though. So sorry for your losses.

The tank was incredible by the way. I'm a dog owner and that hits home hard also. Hope you get it all sorted with insurance and can return to reefing as soon as the situation allows.
 

C4ctus99

Well-Known Member
Review score
+0 /0 /-0
View Badges
Joined
Jan 5, 2023
Messages
632
Reaction score
524
Review score
+0 /0 /-0
Location
Jacksonville
Rating - 0%
0   0   0
I agree, but GFCI will only protect against electrocution. A better option might be to replace the circuit breakers for the outlets around the tank with dual AFCI/GFCI breakers. The arc fault breaker is designed to protect against fires by shutting off power to the circuit if it detects arcing, (like could occur from corroded wiring around a tank), which can create enough heat to start a fire. They run about $60, but replacing circuit breakers isn't a DIY project for many people (and probably shouldn't be for most people). According to my electrician, AFCI breakers have been required in new construction for most living area circuits for a couple of decades.

I have State Farm insurance and they sent me a Ting device, which monitors all the circuits to detect arcing and other problems that could cause a fire. They pay for the monitoring the first 3 years, I think it is.
Kinda, GFCI tests the inbound current against the outbound current, if there’s any difference it trips. So if an arc either causes a difference in current on the hot and neutral or actually arcs to ground, I will still trip.

Arc fault is specifically for this, but they have really bad nuisance tripping which could kill everything in your tank way sooner, but keep your house intact. I installed an dimmer switch in a guys house for him and had to replace the breaker because the switch kept tripping it due to something in the phase dimming mechanism. I’d be concerned about putting heaters and switches motor loads on it as the internal arcing and power draw could create a similar situation on an AFCI
 
Nutramar Foods

ReefDreamz

Active Member
Review score
+0 /0 /-0
View Badges
Joined
May 14, 2008
Messages
249
Reaction score
296
Review score
+0 /0 /-0
Rating - 0%
0   0   0
Kinda, GFCI tests the inbound current against the outbound current, if there’s any difference it trips. So if an arc either causes a difference in current on the hot and neutral or actually arcs to ground, I will still trip.

Arc fault is specifically for this, but they have really bad nuisance tripping which could kill everything in your tank way sooner, but keep your house intact. I installed an dimmer switch in a guys house for him and had to replace the breaker because the switch kept tripping it due to something in the phase dimming mechanism. I’d be concerned about putting heaters and switches motor loads on it as the internal arcing and power draw could create a similar situation on an AFCI
Do EDP breakers protect against fires?
 

Troylee

all about the diy!!!!!
Review score
+0 /0 /-0
View Badges
Joined
Jan 15, 2010
Messages
14,534
Reaction score
4,679
Review score
+0 /0 /-0
Location
Vegas baby!!!!
Rating - 0%
0   0   0
Sorry for your losses! That really sucks! I just saw not to long ago locally the same thing happened and a eb832 caught fire and burned his whole set up down..
IMG_0030.jpeg
 
Last edited:
World Wide Corals

areefer01

Valuable Member
Review score
+0 /0 /-0
View Badges
Joined
Jun 28, 2021
Messages
1,738
Reaction score
1,778
Review score
+0 /0 /-0
Location
Ca
Rating - 0%
0   0   0
Sorry for your losses! That really sucks! I just saw not to long ago locally the same thing happened and a eb832 caught fire and burned his whole set up down..View attachment 3165806

Unless there has been an update Terrence didn't say what caused his fire nor did he say it was related to the controller equipment.
 

Ann Enomy

Community Member
Review score
+0 /0 /-0
View Badges
Joined
Oct 4, 2019
Messages
64
Reaction score
74
Review score
+0 /0 /-0
Rating - 0%
0   0   0
Also GFCI those outlet kids.
I agree, Unfortunately I had a tank crash due to a GFCI tripping and it was recommended by a few to remove the GFCI. Seeing this post makes me think the hassle I went through is nothing and at least I did't loose my business (waiting room tank) due to a fire.
 

C4ctus99

Well-Known Member
Review score
+0 /0 /-0
View Badges
Joined
Jan 5, 2023
Messages
632
Reaction score
524
Review score
+0 /0 /-0
Location
Jacksonville
Rating - 0%
0   0   0
Do EDP breakers protect against fires?
That works the same way as a GFCI, just not as fast. The GFI will trip at 5 or 6mA, EDPs trip at a greater current like 30mA.

Neither are fire protection, only ground fault protection, but if a ground fault is what started the fire, or something in the arcing causes symptoms similar to a ground fault, then it will trip and kill power.

AFCI breakers are specifically to protect against arcing (the primary source of fires) but there are a lot of downsides and nuisance tripping with them, I personally would not trust my tank on one…
 
Nutramar Foods

C4ctus99

Well-Known Member
Review score
+0 /0 /-0
View Badges
Joined
Jan 5, 2023
Messages
632
Reaction score
524
Review score
+0 /0 /-0
Location
Jacksonville
Rating - 0%
0   0   0
I agree, Unfortunately I had a tank crash due to a GFCI tripping and it was recommended by a few to remove the GFCI. Seeing this post makes me think the hassle I went through is nothing and at least I did't loose my business (waiting room tank) due to a fire.
I think GFCIs are only good for 5-10 years, then they can have nuisance tripping issues. Also, high motor loads can sometimes cause symptoms similar to a ground fault, causing it to trip
 

areefer01

Valuable Member
Review score
+0 /0 /-0
View Badges
Joined
Jun 28, 2021
Messages
1,738
Reaction score
1,778
Review score
+0 /0 /-0
Location
Ca
Rating - 0%
0   0   0
AFCI breakers are specifically to protect against arcing (the primary source of fires) but there are a lot of downsides and nuisance tripping with them, I personally would not trust my tank on one…

There are a few downsides for sure. Rapid on/off or similar turn on inrush. I've personally seen my display heater(s) doing this. Also my home stereo / amplifier.
 

wjm6449

Community Member
Review score
+0 /0 /-0
View Badges
Joined
May 5, 2023
Messages
66
Reaction score
140
Review score
+0 /0 /-0
Location
new jersey
Rating - 0%
0   0   0
I think GFCIs are only good for 5-10 years, then they can have nuisance tripping issues. Also, high motor loads can sometimes cause symptoms similar to a ground fault, causing it to tr

even if. If my fellows here are doing plumbing replacing a gfci outlet is as easy as you get for electrical work.
 
Nutramar Foods

workhz

Well-Known Member
Review score
+0 /0 /-0
View Badges
Joined
Apr 23, 2021
Messages
974
Reaction score
1,097
Review score
+0 /0 /-0
Location
nova
Rating - 0%
0   0   0
Sorry for your loss. So lesson here is put a smoke detector right by the tank, with wireless notifications? Not sure that’s a huge help when you are away but might buy enough time to call 911.
 
AS
OP
OP
Ctownjlo

Ctownjlo

New Member
Review score
+0 /0 /-0
View Badges
Joined
Oct 4, 2021
Messages
22
Reaction score
22
Review score
+0 /0 /-0
Location
Washington
Rating - 0%
0   0   0
Sorry for your loss. So less here is put a smoke detector right by the tank, with wireless notifications? Not sure that’s a huge help when you are away but might buy enough time to call 911.
Someone on another post showed me these grenades used in kitchen that fires in kitchens. He was a firefighter and said he's seen them knock down fires.
 
www.dinkinsaquaticgardens.com

workhz

Well-Known Member
Review score
+0 /0 /-0
View Badges
Joined
Apr 23, 2021
Messages
974
Reaction score
1,097
Review score
+0 /0 /-0
Location
nova
Rating - 0%
0   0   0
Someone on another post showed me these grenades used in kitchen that fires in kitchens. He was a firefighter and said he's seen them knock down fires.
Interesting, I just looked them up. I feel like I need to buy about 50 of them. Wonder what kind of testing has been done on them. Wouldn't hurt to have a few of them here and there.
 

Troylee

all about the diy!!!!!
Review score
+0 /0 /-0
View Badges
Joined
Jan 15, 2010
Messages
14,534
Reaction score
4,679
Review score
+0 /0 /-0
Location
Vegas baby!!!!
Rating - 0%
0   0   0
Unless there has been an update Terrence didn't say what caused his fire nor did he say it was related to the controller equipment.
Jay Moran has posted this a few times blaming the apex.. not sure
 
BRS

Polyp polynomial: How many heads do you start with when buying zoas?

  • One head is enough to get started.

    Votes: 27 10.6%
  • 2 to 4 heads.

    Votes: 145 57.1%
  • 5 heads or more.

    Votes: 65 25.6%
  • Full colony.

    Votes: 10 3.9%
  • Other.

    Votes: 7 2.8%

New Posts

Back
Top