I've replaced the two batteries on my tank which are responsible for keeping the system running during power outages.
The batteries are (2) Duralast deep cycle marine batteries, each rated at 65 amp hours.
I have them connected in parallel for a total of 130 amp hours and have cross connected the charger so that it functions as one battery.
For the purposes of this thread, I will call the total power consumption of devices on the tank 1000watts (1kW). In actuality, its 991watts.
I am surprised to see that the backup barely provides 1 hour of support.
The lights are Hydra 32s and according to the website, have a power consumption of 90watts. I have 3 for a total of 270watts. If I move them to the grid side, I save a lot of power but sacrifice light during a power outage. I could also move only (2) to the grid side and have one, on backup.
Additionally, I have (2) 300watt titanium heaters in the sump for a total of 600watts. If I place these on the grid side, along with all 3 lights, my support hours go up to 4.5 hours. But moving one heater to the grid side will be a good amount of work as it will require 2 temperature controllers, one for each heater.
So, I am interested in hearing other perspectives and how you would deploy this resource on your tank.
Thank you,
Dom
The batteries are (2) Duralast deep cycle marine batteries, each rated at 65 amp hours.
I have them connected in parallel for a total of 130 amp hours and have cross connected the charger so that it functions as one battery.
For the purposes of this thread, I will call the total power consumption of devices on the tank 1000watts (1kW). In actuality, its 991watts.
I am surprised to see that the backup barely provides 1 hour of support.
The lights are Hydra 32s and according to the website, have a power consumption of 90watts. I have 3 for a total of 270watts. If I move them to the grid side, I save a lot of power but sacrifice light during a power outage. I could also move only (2) to the grid side and have one, on backup.
Additionally, I have (2) 300watt titanium heaters in the sump for a total of 600watts. If I place these on the grid side, along with all 3 lights, my support hours go up to 4.5 hours. But moving one heater to the grid side will be a good amount of work as it will require 2 temperature controllers, one for each heater.
So, I am interested in hearing other perspectives and how you would deploy this resource on your tank.
Thank you,
Dom