My issues were the following: the auto detect on port 1 and 2 was not optical, it was water on floor. I had to manually change this. I also thought the water line was supposed to be BETWEEN the 2 optical sensors, in the sump.
This is a pretty common misconception.
As you've figured out, the water level should cycle above and below the lower sensor.
You can set up alarms that tell you if the low sensor isn't opening and closing on a regular basis, as it should.
High sensor is emergency backup; it should never be closed under normal operation.