2hp jbj commercial chiller help

zdad_2004

New Member
View Badges
Joined
Sep 11, 2022
Messages
3
Reaction score
0
Location
U.S.
Rating - 0%
0   0   0
I have a 2hp jbj commercial chiller and I was seeing if anyone could help me in making sure I get it wired correctly. Says it needs 208/230volt power source. I thought I would need a 2 pole breaker and 4 cable wire to install 240 volts. I only see 3 spots on the bottom here to hook up the wires. Any know how this should be hooked up and what I would need? Thanks in advance
1000006481.jpg
 

Subsea

5000 Club Member
View Badges
Joined
Jun 21, 2018
Messages
5,658
Reaction score
8,176
Location
Austin, Tx
Rating - 0%
0   0   0
When running 220VAC it is only necessary to have 3 wires: 2 hot wires and one ground. You are correct about 2 pole breaker.

Inside the circuit breaker distribution panel, both neutral & ground are on the same bus. There is the fourth leg/wire you were looking for.
 
Last edited:

HAVE YOU EVER KEPT A RARE/UNCOMMON FISH, CORAL, OR INVERT? SHOW IT OFF IN THE THREAD!

  • Yes!

    Votes: 32 45.7%
  • Not yet, but I have one that I want to buy in mind!

    Votes: 9 12.9%
  • No.

    Votes: 26 37.1%
  • Other (please explain).

    Votes: 3 4.3%
Back
Top