Was running my salt mixing pump and heater for a water change. Poked my finger in to get a little hint on temp, felt a tingle.
IMG_0916.jpeg
It was reading 80VAC before I took the picture. But I’m grounded on a stainless workbench on steel legs sitting on concrete so not the best ground source. Surprised that two different gfci outlets didn’t trip. Don’t need suggestions just don’t have other fish people to share with.
 

tedfisher496

Active Member
View Badges
Joined
Aug 29, 2023
Messages
264
Reaction score
120
Location
Belle Vernon
Rating - 0%
0   0   0
Was running my salt mixing pump and heater for a water change. Poked my finger in to get a little hint on temp, felt a tingle.
IMG_0916.jpeg
It was reading 80VAC before I took the picture. But I’m grounded on a stainless workbench on steel legs sitting on concrete so not the best ground source. Surprised that two different gfci outlets didn’t trip. Don’t need suggestions just don’t have other fish people to share with.
their should not be 2 GFI receptacles on a circuit.
 

tedfisher496

Active Member
View Badges
Joined
Aug 29, 2023
Messages
264
Reaction score
120
Location
Belle Vernon
Rating - 0%
0   0   0
you can wire in parallel as long as you dont wire line to load from one to the other. Why would you want more than one anyway? I just get a gfci and be done.
 
Last edited:

BZOFIQ

5000 Club Member
View Badges
Joined
Jul 31, 2014
Messages
5,049
Reaction score
4,313
Location
NYC
Rating - 100%
9   0   0
you can wire in parallel as long as you dont wire line to load from one to the other. Why would you want more than one anyway? I just get a gfci and be done.

So you can split your loads across multiple GFCIs

Example, if a faulty pump trips one GFCI you only lose wha is's on that GFCI, the rest of the system still works on the other.

I have it set across 5 GFCIs on 3 separate breakers. One pops and the rest keeps running. People put it all one - way too risky.
 

Steve Zee

Community Member
View Badges
Joined
Sep 14, 2022
Messages
44
Reaction score
83
Location
East Coast
Rating - 0%
0   0   0
GFCI’s work by measuring CURRENT not Voltage. Make sure your garage circuit has a GFCI while mixing water. And my pet peeve is why anyone puts relevance on a cheap meter with test leads dropped in the water. It literally means nothing. I can get 60 volts by sticking a probe in a potato on my kitchen counter. That’s with a True RMS meter.

Splitting up your current leakage over multiple GFCI’s is a good idea! Each GFCI is set to trip before the current imbalance reaches 6mA. That’s MILLI-AMPS. A normal house circuit is typically 15 or 20amps. So 6mA (6/1000th of an amp) is barely enough to cause any real current draw. However, because every component has some level of current leakage it degrades your protection circuit by making it even more sensitive. Meaning, if you have multiple devices plugged into one GFCI, you could have a leakage level of 4mA and now one device can trip the circuit with as little as 2mA. More GFCI’s spread this leakage over multiple branches and give more leeway for all devices.

And yes, It’s almost always the heater! Heating coils and expansion from the heat makes it hard to keep waterproof. Never skimp on your heater.
 

KStatefan

2500 Club Member
View Badges
Joined
Jun 24, 2015
Messages
4,560
Reaction score
4,375
Location
MHK
Rating - 0%
0   0   0
you can wire in parallel as long as you dont wire line to load from one to the other. Why would you want more than one anyway? I just get a gfci and be done.

So you do not have a single point of failure
 
OP
OP
FDchase

FDchase

Active Member
View Badges
Joined
Jul 19, 2022
Messages
206
Reaction score
195
Location
Solano
Rating - 0%
0   0   0
GFCI’s work by measuring CURRENT not Voltage. Make sure your garage circuit has a GFCI while mixing water. And my pet peeve is why anyone puts relevance on a cheap meter with test leads dropped in the water. It literally means nothing. I can get 60 volts by sticking a probe in a potato on my kitchen counter. That’s with a True RMS meter.

Splitting up your current leakage over multiple GFCI’s is a good idea! Each GFCI is set to trip before the current imbalance reaches 6mA. That’s MILLI-AMPS. A normal house circuit is typically 15 or 20amps. So 6mA (6/1000th of an amp) is barely enough to cause any real current draw. However, because every component has some level of current leakage it degrades your protection circuit by making it even more sensitive. Meaning, if you have multiple devices plugged into one GFCI, you could have a leakage level of 4mA and now one device can trip the circuit with as little as 2mA. More GFCI’s spread this leakage over multiple branches and give more leeway for all devices.

And yes, It’s almost always the heater! Heating coils and expansion from the heat makes it hard to keep waterproof. Never skimp on your heater.
So the cheap meter gets the job done in the garage. Close enough to ohm out resistance on a throttle body position sensor. Testing this way also showed background voltage for the heater and 2vac on the pump, hardly anything. So yes it was a way to test what was letting off electricity without just feeling for a tingle. Now when I’m working on my elevators we use flukes, would I use my garage meter on a controller that cost more than I make in a year? No. Do I see a point in spending a bunch of money for basic testing around the house and on cars? No. It got the job done and showed me what was giving me the problem.

Also not sure why anyone would put a gfci outlets in series. Also more surprised me grounding out the system by poking my finger in while bare foot didn’t provide enough to trip it.
 

Steve Zee

Community Member
View Badges
Joined
Sep 14, 2022
Messages
44
Reaction score
83
Location
East Coast
Rating - 0%
0   0   0
But did that meter really show you what the problem was? Taking meter readings and making assumptions based on what you perceived to be correct is careless at best. Sorry.

And even suggesting that someone recommended installing GFCI’s in “SERIES” means you misunderstood the advice given because that was never suggested. I own a company the designs, builds, and maintains sophisticated residual current monitors (GFCIs) for broadcast, live events, and motion picture/television electrical systems. I literally troubleshoot residual current problems with hundreds of components all day long everyday. In addition, the last 20 years I’ve dedicated 1000’s of hours helping create national standards regarding how and where GFCI’s and shock protection should be implemented.
So, I just thought I would try and help and possibly keep someone from getting hurt.
So the cheap meter gets the job done in the garage. Close enough to ohm out resistance on a throttle body position sensor. Testing this way also showed background voltage for the heater and 2vac on the pump, hardly anything. So yes it was a way to test what was letting off electricity without just feeling for a tingle. Now when I’m working on my elevators we use flukes, would I use my garage meter on a controller that cost more than I make in a year? No. Do I see a point in spending a bunch of money for basic testing around the house and on cars? No. It got the job done and showed me what was giving me the problem.

Also not sure why anyone would put a gfci outlets in series. Also more surprised me grounding out the system by poking my finger in while bare foot didn’t provide enough to trip it.
 
OP
OP
FDchase

FDchase

Active Member
View Badges
Joined
Jul 19, 2022
Messages
206
Reaction score
195
Location
Solano
Rating - 0%
0   0   0
Second part wasn’t for you. It was a comment on previous posts.

Also I’m not trying to be condescending. Just explaining that I’m not trying to trouble shoot complex electrical systems. Just find what piece of equipment is failing and my test worked. Granted my ground was bad yesterday so here are results from testing again. Pump unplugged
IMG_0922.jpeg
pump plugged in
IMG_0923.jpeg
Even my voltage detector starts alarming the second it gets close to the bin. Just trying to find a simple leak from a bad pump and thought I would share as nobody I talk to would care.
 

nereefpat

7500 Club Member
View Badges
Joined
Apr 20, 2018
Messages
8,185
Reaction score
8,976
Location
Central Nebraska
Rating - 0%
0   0   0
We care. Seems to me that you figured it out. Throw out the bad pump. I've had lots of powerheads do the same thing. Those style seem to fail eventually.
 

Steve Zee

Community Member
View Badges
Joined
Sep 14, 2022
Messages
44
Reaction score
83
Location
East Coast
Rating - 0%
0   0   0
I care. In fact, I just wanted you to be safe since working inside a tank with a bad component is dangerous. So I wanted to make sure you are using a GFCI or you are separating yourself from the water while trouble shooting.

By the way, the tingle is likely less than 6mA. GFCI's do not keep you from getting shocked. They keep you from receiving a dangerous shock. In the household standard "Class A" protection that is below the "Let Go Threshold" that covers everyone including toddlers. The "let go threshold" for adult men is around 20mA. Still not much but double that at around 50mA and you have respiratory arrest.
 

exnisstech

Grumpy old man
View Badges
Joined
Feb 11, 2019
Messages
10,593
Reaction score
15,225
Location
Ashland Ohio
Rating - 0%
0   0   0
Don’t need suggestions just don’t have other fish people to share with


The OP just wanted to share with like minded people not saying no one here cares. No harm in that. My Gals eyes glaze over after a minute or two when I'm trying to explain something tank related lol
 

SteveMM62Reef

Valuable Member
View Badges
Joined
Sep 21, 2020
Messages
2,478
Reaction score
1,590
Location
La Plata
Rating - 0%
0   0   0
I’d get a 24 Vdc Pump for your mixing container, they are a lot Safer, and will quickly pay for themselves in Energy Savings. Also I found I don’t need a Heater in my mixing container, even during the Winter, when it can drop to 66F verses a 76F Aquarium Temperature. There just isn’t enough temperature change, at up to a 25% Water Change to be concerned about.
 
OP
OP
FDchase

FDchase

Active Member
View Badges
Joined
Jul 19, 2022
Messages
206
Reaction score
195
Location
Solano
Rating - 0%
0   0   0
I was planning on that. Getting a sump pump style so it’s easier to do a water change too. Heater is left over from my old tank. I used 5 gallon jugs stored inside and a 5 gallon WC dropped the temp of my tank about 10 degrees one time, so heater was necessary for that.
 